Advice on buying a brand new home > NHBC Warranty

Amtico flooring tolerances

(1/4) > >>

steveball:
We are currently in dispute with our builder and the NHBC about the inconsistency in the level of the floor post the Amtico flooring being installed. We instructed our builder to complete a survey as we were not happy with the unevenness, and they were only happy to repair one part of the floor. Due to this we instructed the NHBC who I believe are not conforming to the correct guidelines when measuring the high\low points of the flooring, although they identified two areas, one of which the builder identified.

The entire of our ground floor is a concrete slab...

To my understanding the standards are as follows

9.1.5 - This is the tolerance of the unfinished floor to +\-5mm
and
9.3.7 - Flexible finish, in our case Amtico is a flexible vinyl and as such has to be installed to the manufacturers guidelines +\-3mm

Amtico have advised, along with the Contract Flooring Association, the flooring is to be installed on a concrete screed to BS8203 SR1 (this is +\-3mm) however the NHBC are saying it is their guidelines which are to be followed, and they are using +\-5mm which I can only assume is related to 9.1.5 - an unfinished floor. This information has been emailed to the NHBC as an attachment from the manufacturer.

Over multiple emails, I have asked the NHBC to clarify why they are choosing to ignore the wording in standard 9.3.7, where the flooring should be installed to the manufacturers specification - sadly they keep ignoring this item and continue to state they measured to the correct standard, a standard they wont confirm the specification of, apart from +\-5mm and it has to be reasonably level.

When the NHBC measured the floor it was at the maximun +5mm tolerance, which is over the 3mm it should be. The other issue is when measuring they used the high points, but didnt offset these against the low points over the 2M length defined in the standard, making the deviation in level looking to be more than 5mm.

If anyone would like to look at some poor quality pictures of mine, here is my dropbox

https://www.dropbox.com/sh/0fdbjr6u24h4kjq/AAC09j_lHo7AKPYNP4z5U_RHa?dl=0

From Amtico

'The quality and preparation of subfloors, testing for moisture content and relative humidity, and installation procedures must be in accordance with Amtico International technical guidelines and country specific standards (BS 8203 and BS 8204 for UK).'

From CFA

'The British Standard (BS 8203, SR1) and the Amtico instructions stipulate that the floor must not deviate by more than 3mm over a 2 metre span. It is also reasonable to expect the smoothing compound will befree from trowel marks and other irregularities caused by poor installation.'

New Home Expert:
Firstly and most important - Who is the housebuilder?

The only applicable standard regarding the NHBC warranty will be their own "A consistent approach to finishes"
1.2 S8 states deviation in floor level of 4mm per metre up to 6 metres floor or 25mm maximum out of level above this.  There is also the + or - 5mm per 2 metres you mention.

Given the fact that it has been agreed to do part of the floor, I wonder why given the work and upheaval required, they are arguing about the flooring that is right on the maximum of the NHBC standard 5mm tolerance.

Finally, it is also incumbent on all following trades, to fully inspect the surfaces they are working with and either bring any poor workmanship to the site managers attention and refuse to work on it, or correct defects, in this case by adding latex floor levelling compound.

My opinion is and has always been if it looks right it is and if it is wrong it should be sorted regardless of tolerance. You would by a car that had tolerances like this!


steveball:
The builder is David Wilson and I am not here to name and shame.

Would it help if I were to save the report to my Dropbox for you to assess?

The reason I mentioned 9.1.5 and 9.3.7 is due to that’s what my floor was being measured against in the session I had with the NHBC.

The bit I don’t get is where they only measured the high points, and it was quite obvious the low points within the same 2M were pretty obvious. I assume thats why the tolerance is set to +/-5mm

New Home Expert:
It is vital if housebuilders are ever going to be forced to change, that buyers with genuine issues post them online, here and elsewhere, for all time naming and shame builders, especially plc housebuilders and bring the problems faced by homebuyers to government notice.

Never mind Dropbox I've had lots of posts with links to Dropbox that then a few years later don't work. Cut and past the report or take a photo of it and post.

A plus or minus tolerance of 5mm is a total of 10mm.

steveball:

--- Quote from: New Home Expert on September 03, 2018, 06:32:05 am ---It is vital if housebuilders are ever going to be forced to change, that buyers with genuine issues post them online, here and elsewhere, for all time naming and shame builders, especially plc housebuilders and bring the problems faced by homebuyers to government notice.

Never mind Dropbox I've had lots of posts with links to Dropbox that then a few years later don't work. Cut and past the report or take a photo of it and post.

A plus or minus tolerance of 5mm is a total of 10mm.

--- End quote ---


I have attached the report minus my details, we believe that due to there being a foreign object under the flooring, this should be good enough to have the flooring lifted - due to not being clear of debris and what is the rest of the slab like?