Positioning of Air Bricks and DPC?
« on: June 18, 2018, 10:49:21 am »
Please could someone provide some advice with regards to the position of the air bricks and DPC in relation to the landscaping at the front of my property? The DPC is located directly on top of the air bricks.

Is this an acceptable level above the ground to avoid any adverse damp issues?

Many thanks in advance.




michaelmge

  • Junior Member
  • **
  • Posts: 30
Re: Positioning of Air Bricks and DPC?
« Reply #1 on: June 18, 2018, 09:17:24 pm »
Had the same problem with my Bloor Home. Building regulations and technical manual require the dpc to be 150mm above finished ground level. They should dig it out and reduce the ground level and put gravel in. The top of the gravel will then be the new ground level. Also the dpc should be revealed as mortaring over the top causes  a breach of the Dpc.

Tim Fee Snagging Inspector

New Home Expert

  • Global Moderator
  • Guru member
  • *****
  • Posts: 1625
  • Country: england
  • Expert advice for new home buyers
    • New Home Blog
Re: Positioning of Air Bricks and DPC?
« Reply #2 on: June 19, 2018, 05:59:14 am »
As said, DPC should be a minimum of 150mm above finished ground level.
And yes, most of the time the Air bricks for under floor ventilation are directly beneath the dpc.
New Home Blog - New Home Expert is committed to providing help and advice for people having issues with their new homes and difficulties with house builders as well as helping potential buyers reduce the risk of possible problems if they do buy.

AOIS

  • New Member
  • *
  • Posts: 23
Re: Positioning of Air Bricks and DPC?
« Reply #3 on: June 19, 2018, 04:30:35 pm »
Thank you for the advice.

Please could you confirm if the bottom of the air brick should be at least 150mm above ground level?

AOIS

  • New Member
  • *
  • Posts: 23
Re: Positioning of Air Bricks and DPC?
« Reply #4 on: June 19, 2018, 05:49:16 pm »
I have attached a couple of further images and outlined the DPC level.

In the first image the door threshold looks to sits directly on the DPC level is this acceptable? The landscaping in the image is level with the bottom of the entrance path across the entire flowerbed and therefore looks as if the DPC is only 1 brick high and therefore under the 150mm NHBC regulation?

Is there also a regulation in terms of what intervals air bricks should be spaced please?

I want to be sure of all my fact before I raise the issue.

Thanks in advance.

New Home Expert

  • Global Moderator
  • Guru member
  • *****
  • Posts: 1625
  • Country: england
  • Expert advice for new home buyers
    • New Home Blog
Re: Positioning of Air Bricks and DPC?
« Reply #5 on: June 20, 2018, 12:46:56 pm »
In reality, the top of the airbrick is 150mm above finished ground level.
It should be any lower! (bottom 75mm minimum above FGL.)

The dpc is always under the door threshold so this is OK

Airbricks are spaced at 1.5 - 2m centres at least 600mm for a corner and not under a door or patio door.
NHBC Standards Technical Guidance 